If you are sizing a motor load and let’s say you figure your load will draw 28
Before voltage drop is considered, a 28A motor load must be efficiency adjusted x 1.25 per 220.18(A)
28A x 1.25 = 35A
Then any voltage drop calc must include Table 9 Note 2 Power Factor (PF) formula, per 460.9, to match PF built into all NEC Tables, including 310.16 ampacity.
Skipping both requirements, without engineered plans, under sizes equipment loads shown in 220.18, and other inductors.
Typical resistive loads don't require these motor inductive adjustments, so it is possible that dumb luck gets those wire sizes right.
However, given the complexity and experience required to properly adjust NEC 310.15 ampacity tables for extra-environmental variables, few inspectors are capable of correcting these errors, much less inductive motor-loads errors.
Its too complex, so it perpetuates the cottage industry of thermal imaging.
Thermal imaging is the Industry standard for inspecting NEC ampacity-table errors, so wire can be ripped out and replaced immediately after installed.