Hi,
I'm sure that this has been overdone, but any clarification is appreciated. To size conductors, I assume that three calculations/factors need to be considered:
Also, if I understand this correctly, the 125% multiplier does not apply to numbers 1 and 3, but only to number 2. Is this correct?
Am I missing any other major consideration?
I'm sure that this has been overdone, but any clarification is appreciated. To size conductors, I assume that three calculations/factors need to be considered:
- The temperature rating of the terminals cannot be exceeded (110.14(C)).
- The nature of the load must be considered; that is, continuous vs. non-continuous (210.19(A)(1)(a)).
- The conditions of use (ambient temperature adjustment and correction factors for the number of current-carrying conductors---viz. what used to be called derating) (210.19(A)(1)(b))
Also, if I understand this correctly, the 125% multiplier does not apply to numbers 1 and 3, but only to number 2. Is this correct?
Am I missing any other major consideration?