I run into this quite often, where someone, often more knowledgeable than myself, will tell me that they always use a certain conductor size for a specific amperage, and the way I read it, they are one size too small.
Rep from PG&E I was talking to today about a couple upcoming projects I have, one of them being a multi unit meter stack, with 4 individual 100A breakers and a 400A rated buss. I have it sized for 600 mcm for the service conductors, PG&E guy told me “everyone always uses 500’s for those 400A.”
It’s happened a few more times recently, like guys using 2/0 for 200A commercial feeders or services. Commercial can’t take advantage of 310.12
I believe that if the load Calc comes out to some amount that would allow the smaller conductor, then the next size up standard size breaker could be used, however, that doesn’t really work out for 2/0 as 175A Breakers are common.
Is there something I’m missing here?
Rep from PG&E I was talking to today about a couple upcoming projects I have, one of them being a multi unit meter stack, with 4 individual 100A breakers and a 400A rated buss. I have it sized for 600 mcm for the service conductors, PG&E guy told me “everyone always uses 500’s for those 400A.”
It’s happened a few more times recently, like guys using 2/0 for 200A commercial feeders or services. Commercial can’t take advantage of 310.12
I believe that if the load Calc comes out to some amount that would allow the smaller conductor, then the next size up standard size breaker could be used, however, that doesn’t really work out for 2/0 as 175A Breakers are common.
Is there something I’m missing here?