By Mike Holt for EC&M Magazine
Q 1. I have a question on the application of the conductor ampacity adjustment factors contain in 310.15 (B)(2). When adjusting conductor ampacity, do we use the conductor ampacity based on the 90?C insulation rating (for THHN) or the 75?C temperature rating of the equipment terminals?
A 1. When adjusting conductor ampacity, use the temperature rating of the conductor, not the equipment terminals [110.14(C)
The above Q & A was extracted from the web, which appares to be an interview, or extracted from a forum.
The reason I'm displaying this is because I'm a little bit confused when it comes to sizing feeder conductors & overcurrent protection.
Now, if you compare the above Q & A with the following, can someone tell me if the conductor was sized based on the (inverse-time breakers 75*c terminal rating) or because the ampacity is over 100A, thus the ampacity must be based on the provisions of 110.14 C. which states, circuits rated over 100A or marked for conductors larger than 1 AWG, shall be used only for the following: (1) conductors rated 75* C.
Q. What size feeder conductor (THHN) and protection device (inverse-time breaker 75*C terminal rating) for the following loads: 46.2A X 1.25% + 30.8A + 30.8A + 16A = 136A
From table 310.16 the answer that was given was 1/0 AWG for the above question, I ask again, was this answer derived from the terminal rating of the device or by following article 110.14 C
I would really appreciate if someone can enlighten me, thanks!
Ceiba