I just got comments back from the electrical inspector:
SHOW COMPLIANCE WITH NEC 2008 ARTICLE 240.21 YOUR SECONDARY TAP CONDUCTOR OF
500KCMIL IF FUSED AT 400AMP AS 240.21 REQUIRES YOUR SECONDARY CONDUCTORS TO
MEET OR EXCEED THE SECONDARY OVERCURRENT DEVICE.
I have a 480-120/240 v 75 kVA transformer with 500 kcmil conductors. I have 200A fuses on the disconnect on the primary side. There are 400A fuses in the disconnect between the transformer and the panel.The loading on the panel is 236 amps at 240 volts.
I'm using Mike's "Commercial and industrial Wiring and Raceway Chart". What do I have to do to get in compliance with this inspector?
Jack