I need some help with clarification on conductors in a PV system. My understanding is that the conductors that come from the panels/strings to the dc combiner box are sized at 156% to account for the open circuit current adjustments (as well as the string fuses). Now to address the dc conductors from the combiner to the inverter. The information I have is that the conductors do not need to be rated at 156% because when the system is not under load there is no current flowing through the conductors so there is no need for the adjustment and the fuses will protect the strings. The only adjustment the dc conductors to the inverter need is a 125% multiplier for the continuous load factor. Is this line of thinking correct ? If is not where do I find the correct calculations and information at ?