i don't think you can determine the actual problem causer.. imo-- as a thermographer i have delt with plenty of splice problems before they failed. there is a therory about splices and electrical connections that i believe in.
an electrical connection when properly made with approved materials and with proper torque applied will not fail unless overloaded.
years ago maintainance programs practiced having their electricians re-torque wire connections every two years---they found out over the years that this caused more problems because they were "over torquing" the connections causing additional problems! once a connection is made and properly torqued it should remain good. now, comes a connection that is overloaded every once in a while. the wire over-expands each time while overloaded and then begins to fail--loser-hotter-loser-hotter-etc.. the splicing of aluminum and copper as been used for years and if the materials used are designed for al/cu and properly cleaned-knoloxed and torqued will last. i would suspect the splice in question was either not made correctly or overloaded at times...