Which section of NEC deals with the taps of conductors from bus-bar; is it allowed that for short length, a cable is run from a panel to a load without a breaker in the panel. Thanks
Would it be a tap if it does not leave the enclosure? If it does then it will need an ocpd where the tap terminates 240.21***Which section of NEC deals with the taps of conductors from bus-bar; is it allowed that for short length, a cable is run from a panel to a load without a breaker in the panel. Thanks
Which section of NEC deals with the taps of conductors from bus-bar; is it allowed that for short length, a cable is run from a panel to a load without a breaker in the panel. Thanks
MCC Bus
I do not have much experience with MCC's but as far as I now what you propose would be no different that tapping the bus bar of a panelboard, bussed gutter, or busway. Look at the definition of "feeder" and the tap rules in 240.21. Also you may want to consider 110.3(B). A picky inspector could require approved lugs from the manufacturer and possibly even their overall approval.
I agree. Tapping the buss on any factory assembly is frowned upon by most inspectors (altering listed equipment) unless authorized by the manufacturer.
In any event, taps would be covered by 240.21
If the tap conductor runs from the MCC to a load which has its own main breaker, then the conductor will still be protected by the breaker; the only difference would be that the breaker would be located inside the load-cabinet instead of inside the MCC. Is this arrangement allowed by NEC 240.21(2)(2)?