Conductor temperature, insulation, and voltage rating

Status
Not open for further replies.

DEW202001

Member
Location
ODENTON, MD
Do conductors temperature, insulation, and voltage rating all have to be the same to be installed in a raceway? Thanks


Sent from my iPhone using Tapatalk Pro
 

texie

Senior Member
Location
Fort Collins, Colorado
Occupation
Electrician, Contractor, Inspector
No. As long as your calcs for temp are using the lowest rated conductor or for the voltage, use the lowest rated conductor. Typically, the voltage is not a consideration as in this context all the conductors will be 600 volt rated.
 