I am supplying a 120Vac 12Fla motor over a distance that requires the use of #6awg Cu to assure an acceptable level of voltage drop.
I want to use a single pole 20 CB. This brought up the question of wire size vs terminal size. Any comments?
 

cowboyjwc

Moderator
Staff member
Location
Simi Valley, CA
I had the same problem once on a long run had to run #2 to keep the voltage up for a 60 amp panel. I ran to a pull box just below the panel and then installed #6's up to the breaker.

My point, of course is, if the wires wont fit under the terminal, then I would just pigtail a piece of #12 to it and hook it up. Ypu've covered the voltage drop and a 6" piece of wire isn't going to make that much difference.
 

PAW2006

Member
Location
Upstate NY
Thanks guys, That's the only way I could think to do it. I just haven't come across this before. As long as the OCPD is sized for the smaller wire I should be good.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
360Youth said:
I would say the same. J-box mounted at your panel and reduce the wire size to accomodate terminal size.

Why waste a J-box? I would splice it right in the panel.
 

winnie

Senior Member
Location
Springfield, MA, USA
Occupation
Electric motor research
Have you considered changing the motor (or just the motor connections) to 240V? For the same % voltage drop at the same _power_ consumption (meaning 1/2 the current) you need wire with 1/4 the cross section, or 12ga rather than 6ga....

-Jon
 

PAW2006

Member
Location
Upstate NY
"Have you considered changing the motor"
Yes, that was the first thing I tried. The motor is an integral part of a pump that is spec'd by the mechnical guys. "It's the only one we can use"
;)
 

cowboyjwc

Moderator
Staff member
Location
Simi Valley, CA
infinity said:
Why waste a J-box? I would splice it right in the panel.

I agree with infinity. I simply used one because I couldn't get the conduit to bend tight enough to get it into the panel, but I could fish a piece of cable down the wall and keep the install fairly clean.
 

360Youth

Senior Member
Location
Newport, NC
infinity said:
Why waste a J-box? I would splice it right in the panel.


I am just refering to situations where you may not have the room. I go a little excessive at times for the sake of neatness. I have "issues" sometimes. :D
 

220/221

Senior Member
Location
AZ
Install a lug on the CB terminal screw or under the CB lug?

It would aggrevate my OCD to have a piece of #12 in there at the start of the circuit.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
PAW2006 said:
I am supplying a 120Vac 12Fla motor over a distance that requires the use of #6awg Cu to assure an acceptable level of voltage drop.
I want to use a single pole 20 CB. This brought up the question of wire size vs terminal size. Any comments?

Okay I will be the pest-- Did you remember to upsize your EGC to #6 or is this in metal conduit?
 