Conductor to large for terminal

Status
Not open for further replies.

Butler

Member
When installing a 100 amp breaker with 2AWG SE cable feeding a 100 amp sub-panel the neutral bar terminals in the dwelling unit 200 amp panel are not large enough for the 2 AWG aluminum SE cable conductor. What is the proper wiring method?
 
Butler, your installing electrician should know where to get the propper lug

Roger
 
Butler said:
When installing a 100 amp breaker with 2AWG SE cable feeding a 100 amp sub-panel the neutral bar terminals in the dwelling unit 200 amp panel are not large enough for the 2 AWG aluminum SE cable conductor. What is the proper wiring method?

Just so you know, you cannot use a 100 amp breaker on #2 SE cable unless it is a feeder... and since you said it was for a sub-panel, the biggest breaker you can use is a 90 amp...
 
Cutler Hammer used to make an adapter that connected to two screws in the neutral bar and then had a lug for a large conductor. A device such as that may be available. I also believe that T&B makes a device that would allow you to connect a copper pigtail to your aluminum wire. The copper conductor may be enough smaller to fit your existing lugs.
 
Butler,

A 'sub panel' needs 4 conductors, Type SE cable has 3, unless it is SER

type cable your installation is NOT code compliant.
 
lug

lug

Square D has a lug adaptor for your scenario which will accomodate the #2 on the ground bar that you would have to install in a sub-panel. Most of them you'll need to remove two screws and add this lug which has two feet to go into the ground bar, problem solved.:grin:
 
benaround said:
Butler,

A 'sub panel' needs 4 conductors, Type SE cable has 3, unless it is SER

type cable your installation is NOT code compliant.
Unless it is for 240 Volt loads only, where no neutral condcutor is needed, such as a large heat pump scenerio.
 