Hey all!
I'm on a project where a building (#1) has a feeder that feeds another building (#2). At the point where the feeder enters building #2 is a pull box; from the pull box the feeder keeps traveling further inside building #2 to a switchboard that serves the building. We have to relocate the pull box / the point of entry where the feeder enters building #2. However, I believe that instead of a new pull box located at the new point of entry for building #2, it should actually be an unfused disconnect switch, based on section 225.31 in the 2008 NEC. This would comply with the requirement for disconnecting all the ungrounded conductors entering a building. Would this be correct? Looking for feedback. This building was built maybe in the 70's or 80's, so i'm not sure if the code required a switch back then.
Thanks!
I'm on a project where a building (#1) has a feeder that feeds another building (#2). At the point where the feeder enters building #2 is a pull box; from the pull box the feeder keeps traveling further inside building #2 to a switchboard that serves the building. We have to relocate the pull box / the point of entry where the feeder enters building #2. However, I believe that instead of a new pull box located at the new point of entry for building #2, it should actually be an unfused disconnect switch, based on section 225.31 in the 2008 NEC. This would comply with the requirement for disconnecting all the ungrounded conductors entering a building. Would this be correct? Looking for feedback. This building was built maybe in the 70's or 80's, so i'm not sure if the code required a switch back then.