I In-spector Member Location New Jersey/Pa Mar 12, 2015 #1 Is a single conductor, THHN/THWN-2 rated for cable tray? If so, where in code can I find info to support this?
Is a single conductor, THHN/THWN-2 rated for cable tray? If so, where in code can I find info to support this?
ces Member Location Northern California, USA Mar 12, 2015 #2 No, tray cable is rated for tray. Sent from my iPad using Tapatalk
don_resqcapt19 Moderator Staff member Location Illinois Occupation retired electrician Mar 12, 2015 #3 In-spector said: Is a single conductor, THHN/THWN-2 rated for cable tray? If so, where in code can I find info to support this? Click to expand... Many single conductors 1/0 and larger are suitable for use in cable tray (in industrial installations) and are marked as such. See 392.10(B)(1).
In-spector said: Is a single conductor, THHN/THWN-2 rated for cable tray? If so, where in code can I find info to support this? Click to expand... Many single conductors 1/0 and larger are suitable for use in cable tray (in industrial installations) and are marked as such. See 392.10(B)(1).
ces Member Location Northern California, USA Mar 12, 2015 #4 don_resqcapt19 said: Many single conductors 1/0 and larger are suitable for use in cable tray (in industrial installations) and are marked as such. See 392.10(B)(1). Click to expand... Great to learn thank you
don_resqcapt19 said: Many single conductors 1/0 and larger are suitable for use in cable tray (in industrial installations) and are marked as such. See 392.10(B)(1). Click to expand... Great to learn thank you