I have recently been given the task to size out a chiller that will be replacing the 30 year old existing.I am really not confident in the process.
The ratings are as follows;
450 ton 460v/3ph/60hz
JOB FLA 381
MOTOR FLA 371
LRA 2598
INRUSH 381
MIN CIRC AMPS 476
MAX FUSE 800
I will use the MCA-476a to size the conductors,I want to run parallel conductors.
350kcmil are good for 240a continuous @75 degrees?
What am I missing. Thanks for your help.