Article 725.49(B), 2008, says that for Class 1 circuit conductors, "Insulation on conductors shall be suitable for 600 volts. Conductors larger than 16 AWG shall comply with Article 310. Conductors in sizes 18 AWG and 16 AWG shall be type..."
Are those literally the only insulation types that are permitted? Or is Article 725 understood to be a supplement or modification to Article 310... so that the conductor types found in Article 310 could also be used?
Are those literally the only insulation types that are permitted? Or is Article 725 understood to be a supplement or modification to Article 310... so that the conductor types found in Article 310 could also be used?