- Location
- Lockport, IL
- Occupation
- Semi-Retired Electrical Engineer
Anybody know of either a ?good design practice? or an actual NEC requirement related to the conductors between a Variable Frequency Drive (VFD) and the motor it serves? Specifically, do you need to use a conductor of a higher rated insulation system (e.g., a 1000V insulation, instead of the 600V used upstream of the VFD)?
This came up in a design discussion with a client who thinks the high level of harmonics generated by the VFD would damage the insulation, if the insulation system did not have a higher rating. He did not think this applied to the conductors from the branch panel to the VFD.
Can anyone confirm or refute the existence of such a requirement?
This came up in a design discussion with a client who thinks the high level of harmonics generated by the VFD would damage the insulation, if the insulation system did not have a higher rating. He did not think this applied to the conductors from the branch panel to the VFD.
Can anyone confirm or refute the existence of such a requirement?