We are doing a project that involves refeeding a fire pump with a new ATS. There is some confusion in the interpretation of this code.
1)My interpretation of this code section is:
NEC 695.6(A), the exception: requires the load conductors from the ATS to be routed outside the building or routed according to 230.6(1),
1) under 2" of concrete beneath the building or
2) encased in 2" of concrete or brick in a chase.
The 2 hour fire rating pertains to the wiring beyond the final point of disconnect (circuit conductors) NEC 695.6(B).
2) Others are interpreting the code to allow 2 hour fire rated systems for ALL the effected wiring. (not my interpretation)
Which is the correct interpretation of the code, (1) or (2)?
Thank you in advance.
Sheldon