We have approx. 50 duplexes that were built in the early 1980's. The wire used to connect the meter to the service disconnect is #4 Arc Welder Cable. There are no other markings on the cable. My question, does this cable used in this application on a 100 amp service comply with the electric code.

Thanks,
Mike :confused:
 

rick5280

Senior Member
Re: Conductors from meter to main disconnect.

I would venture to say NO, because you are using the cable in a way contrary to it's listing.

Rick
 

nvcape

Senior Member
Re: Conductors from meter to main disconnect.

Is this cable between the meter and breaker inside the manufacturers listed board?
 

earlydean

Senior Member
Re: Conductors from meter to main disconnect.

The permitted wiring methods are listed in 230.43. I don't see any welding cable on the list. I do not believe the code in force in 1980 allowed it then, either. If the Building official is made aware of this, and the building code in force at the time of it's installation forbade it, he is required by law to require the building owner to make the necessary repairs. A code violation is a code violation. There is not a statute of limitations, and the burden lies with the building owner. He may then sue for compensation from whomever, after the repairs are completed.
That's the theory, anyway. In real life this sort of thing never gets addressed until a disaster happens.

Earl
 