Conductors in 1/2" conduit Derating???

Status
Not open for further replies.

pushpenny

Member
Hi all im a newbie and have a question. I have the option of either pulling 9 homeruns in MC cable or three 1/2 inch conduits. If I run the conduits can I run three hots and three nuetrals and 1 ground all number 12 thhn in each conduit and not have to worry about derating? since each circuit has its own neutral i dont have to handle tie and it doesnt matter about what phase they are terminated on correct?

Thanks for any input.
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
If I run the conduits can I run three hots and three nuetrals and 1 ground all number 12 thhn in each conduit and not have to worry about derating?
You would have 6 current carrying conductors in each conduit so you would have to derate but, if your are using a 90 deg insulation you could still use # 12 conductors.

since each circuit has its own neutral i dont have to handle tie and it doesnt matter about what phase they are terminated on correct?

Correct, but it is good practisce to spread the circuits out across the phases.

Roger
 