M morgan3520 Member Location Dallas, TX Occupation Electrical Engineer Thursday at 1:34 PM #1 For the purpose: ampacity for sizing conductors/cables installed in cable tray, is Table 310.17 to be used?
For the purpose: ampacity for sizing conductors/cables installed in cable tray, is Table 310.17 to be used?
don_resqcapt19 Moderator Staff member Location Illinois Occupation retired electrician Thursday at 1:51 PM #2 Sometimes, see 392.80
E Elect117 Senior Member Location California Occupation Engineer E.E. P.E. Thursday at 2:06 PM #3 It depends, but most of the time you are limited to 310.16 ampacities by the nature of where the conductors start or end.
It depends, but most of the time you are limited to 310.16 ampacities by the nature of where the conductors start or end.