goog afternoon, i hope some of you can help me, i have a big question.
i am installing an electrical subestation, the transformer is 300 kva, 13200-220/127 volts, 3 phases, the nominal current on secondary side is 787.29 amp, there are only two 3" pvc conduits, i am considering to install 9 conductors of 350 kcm (3 per phase), 3 conductors of 350 kcm for neutral and 2 conductors of 1/0 awg for equipment grounding.
6 conductors of 350 in one conduit (2 of each phase)and one equipment grounding conductor,
6 conductors of 350 in the other conduit (1 of each phase and 3 for neutral) and one equipment grounding.
am i correct?
if not
what do i have to do?
i am sorry because my english is not good.
i am installing an electrical subestation, the transformer is 300 kva, 13200-220/127 volts, 3 phases, the nominal current on secondary side is 787.29 amp, there are only two 3" pvc conduits, i am considering to install 9 conductors of 350 kcm (3 per phase), 3 conductors of 350 kcm for neutral and 2 conductors of 1/0 awg for equipment grounding.
6 conductors of 350 in one conduit (2 of each phase)and one equipment grounding conductor,
6 conductors of 350 in the other conduit (1 of each phase and 3 for neutral) and one equipment grounding.
am i correct?
if not
what do i have to do?
i am sorry because my english is not good.