PeteHJ

Member
I have a project where the contractor installed conductors in a 208Y/120V switchboard. The conductors are resting against the bus bars. I am afrain that any vibration could damage the conductor over time.

I cannot find anything in the NEC that discourages or disallows conductors resting against the bus bars.
 
II am afrain that any vibration could damage the conductor over time.
Are you also concerned that vibration will cause damage to the conductors inside of a 1-gang box, where just about everything touches them or in a JB where the cover is the only thing keeping them from 'springing out'?
 
wires resting on a buss bar might be a reason for concern. we had a WLI switch with 12470 the C phase was up against the A phase buss and it rubbed the wire to the high voltage shield and caused our power to be out for approx 6 hours. but im sure this took a while to rub through the insulation.
 
Bus bars

Bus bars

I have a project where the contractor installed conductors in a 208Y/120V switchboard. The conductors are resting against the bus bars. I am afrain that any vibration could damage the conductor over time.

I cannot find anything in the NEC that discourages or disallows conductors resting against the bus bars.

can't the wires be supported in a better other than resting on the bus bars?
There must be room in the switch board to keep them off the bus bars.
 