DEW202001
- ODENTON, MD
Is this normal. I have never seen this.
I'd bet dollars to doughnuts those wire nuts are twisted onto the insulation. Violation 110.3(B).
Have you ever seen a manufacturer's instruction for installing a wirenut to a single conductor?
And the second step usually involves the 'joining' of multiple wires.The he first instruction on any packaging I have ever seen says "Strip wire 3/8"." Or something to that effect.
Do the instructions even address the use of the wirenut as an insulator for a single conductor?
I don't know if you spent time twisting tools in the field ...
Yes I have.
It's just, you describe is not a violation of 110.3.
In my experience a lot of wirenuts do not hold on to a single conductor very well at all regardless if the conductor is extends past the insulation.
Also, wire nuts are not listed for use with a single conductor.
The listing for the wire nuts in the pic are for a minimum of 2 #22, up to 2 #10. Not listed for less than two of any conductor.
https://www.idealind.com/content/pdfs/catalogs/wire-connector-catalog.pdf
Look on page 3.