Is it a violation to race conductors through a panelboard without terminating/splicing there?
Is it a violation to race conductors through a panelboard without terminating/splicing there?
Only when the caution flag is out.Is it a violation to race conductors through a panelboard without terminating/splicing there?
Is it a violation to race conductors through a panelboard without terminating/splicing there?
Only when the caution flag is out.
...
and if there is a red flag, you have to stop the racing immediately,
or reset the breaker.
sometimes both.
Is it a violation to race conductors through a panelboard.....
Most of the time, there is no issue with running unrelated conductors through a panelboard. Provided that you meet two conditions:
1. The conductors mixed in any cross section, need to qualify as conductors that you can mix in any other raceway or wiring structure. As an example, mixing service and feeder, or service and branch circuit conductors would not be allowed.
2. Verify that you can do this within reasonable fill and bend curvature limits, so that you can keep the panelboard organized and close the cover without wedging to force fit the wires inside. The NEC prescribes a 40% fill by cross sectional area for this application.