greetings earthlings,

Am I mistaken in believing that all 14/2 or 12/2 NM romex is rated for the 90 degree C requirement? All new wiring must meet that standard of 90 degree C in residential work? Thanks in advance for your time.

ciao,
Fred in Saint Louis MO
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
You can use the 90 degree C rating for derating purposes, but your OCPD can't be larger than the 60 degree C ampacity listed in 310.16.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Pierre C Belarge said:
As a contractor, I am curious why you are asking such a question?


My guess is that someone who works with generators and transfer switches doesn't use much romex.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
infinity said:
You can use the 90 degree C rating for derating purposes, but your OCPD can't be larger than the 60 degree C ampacity listed in 310.16.
You know it can under certain situation.
 