D DARUSA Senior Member Location New York City Nov 19, 2009 #1 Do I have to use a sun-light resistance wire if the conduit is exposed to the sun? If so what code section backs it up?
Do I have to use a sun-light resistance wire if the conduit is exposed to the sun? If so what code section backs it up?
Dennis Alwon Moderator Staff member Location Chapel Hill, NC Occupation Retired Electrical Contractor Nov 19, 2009 #2 DARUSA said: Do I have to use a sun-light resistance wire if the conduit is exposed to the sun? If so what code section backs it up? Click to expand... If the conductor is in the conduit then it is not subject to UV rays or sunlight damage. Standard wire with a W- such as THwn is all that is needed. Let me clarify- If this is a riser and the wires are exposed to sunlight at the top then you may have an issue there.
DARUSA said: Do I have to use a sun-light resistance wire if the conduit is exposed to the sun? If so what code section backs it up? Click to expand... If the conductor is in the conduit then it is not subject to UV rays or sunlight damage. Standard wire with a W- such as THwn is all that is needed. Let me clarify- If this is a riser and the wires are exposed to sunlight at the top then you may have an issue there.