Conductors running in a conduit outside

Status
Not open for further replies.
Do I have to use a sun-light resistance wire if the conduit is exposed to the sun? If so what code section backs it up?
If the conductor is in the conduit then it is not subject to UV rays or sunlight damage. Standard wire with a W- such as THwn is all that is needed.

Let me clarify- If this is a riser and the wires are exposed to sunlight at the top then you may have an issue there.
 