I have a VFD that has a rated input current of 285 amps. The VFD has a 600 amp circuit breaker and overloads in the drive enclosure, and the VFD will be fed from a MCC with a 600 amp circuit breaker. Is it code compliant to size the supply conductors at 1.25 x drive input per 430.122 which would be 500 kcmil, or do the conductors need to be sized for 600 amps so they are protected by the breaker?
I've seen other threads asking a similar question, but came across mixed answers.