conduit and box area

Status
Not open for further replies.

d1reyad

Member
can some one tell me how many 12awg can you put in a 1900 box and does ground count as a wire also for 1/2 3/4 1" emt how many wire can i put in the conduit correct me if am wrong for 12 gauge 1/2" emt 9 wire 3/4 15 wires 1" is 25 wires
 
For a box you only need to count all of the EGC's as one conductor based on the largest EGC in the box. 314.16(B)(5)

For conduit fill all conductors, including any EGC's, within the conduit count towards the fill. Chapter 9, note #3.

For conductor fill you need to know the raceway type, the conductor size and the insulation type to answer your last question. For example for EMT and #12 THHN conductors your maximum conduit fill will be 1/2"-9, 3/4-16, 1"-26. Table C.1
 