Could you please help me in finding out the calss 1 div1 rigid Conduits and cable glands.
Early reply will be appreciated.

Thanks in advance
Manju
 
Could you please help me in finding out the calss 1 div1 rigid Conduits and cable glands.
Early reply will be appreciated.

Thanks in advance
Manju
I don't understand your question, for certain. Would you please elaborate?

The only type of conduit permitted in C1D1 are threaded rigid metal and intermediate steel conduit, with the exception of PVC and Type RTRC if embedded in concrete.

Cable is limited to MI or MC-HL and ITC-HL in industrial locations with restricted public access. You will have to use termination connectors that are listed for C1D1 for the specific type cable. The same is true for any flexible cord installations within the designated area.
 