J jap Senior Member Occupation Electrician Apr 19, 2017 #1 If an extension is made from a conduit system containing an EGC does an EGC have to be installed in the extension or can the metal conduit be used and the EGC left out of the extension? JAP>
If an extension is made from a conduit system containing an EGC does an EGC have to be installed in the extension or can the metal conduit be used and the EGC left out of the extension? JAP>
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician Apr 19, 2017 #2 You can use just the raceway of it qualifies as a EGC.
Ponchik Senior Member Location CA Occupation Electronologist Apr 19, 2017 #3 Agree with the Rob, unless it is job spec or facility requirement.