I am a small manufacturer of Sensory Deprivation Tanks and have run into an electrical reviewer that is saying we cannot run a low voltage flexible cable through a conduit as per NEC rules.
We are wanting to locate our filtration and control equipment (engine) in a separate room from the tank to eliminate sound pollution. To do this we have to run 2 cables between the engine and tank. 1 cable has 16 conductors for the LED light, speakers, buttons, and temp sensors all of which are DC. I do not see any reason this cable cannot be installing in a conduit.
The second cable is for a set of 240v 3 amp heater pads that are installed in the tank. This cable is shielded and I could see a requirement for the conduit and cable but I could convert the wire to MC or something else to send the power.
Both cables are from the same manufacturer with the details listed here: http://www.alliedelec.com/images/products/datasheets/bm/SAB NORTH AMERICA/70039027.pdf
The reviewer is quoting from the NEC book which I do not think references anything related to a manufacturer or product.
I am a small manufacturer of Sensory Deprivation Tanks and have run into an electrical reviewer that is saying we cannot run a low voltage flexible cable through a conduit as per NEC rules.
We are wanting to locate our filtration and control equipment (engine) in a separate room from the tank to eliminate sound pollution. To do this we have to run 2 cables between the engine and tank. 1 cable has 16 conductors for the LED light, speakers, buttons, and temp sensors all of which are DC. I do not see any reason this cable cannot be installing in a conduit.
The second cable is for a set of 240v 3 amp heater pads that are installed in the tank. This cable is shielded and I could see a requirement for the conduit and cable but I could convert the wire to MC or something else to send the power.
Both cables are from the same manufacturer with the details listed here: http://www.alliedelec.com/images/products/datasheets/bm/SAB NORTH AMERICA/70039027.pdf
The reviewer is quoting from the NEC book which I do not think references anything related to a manufacturer or product.