Conduit as EGC in older buildings

Status
Not open for further replies.

tompoff43

Member
Location
Cincinnati
Occupation
Electrical designer
I have a older building that has the conduit being used as the EGC. Now that I’m doing a major remodel do I have to put in ground bus and an EGC conductor with the the feeders?
 

qcroanoke

Sometimes I don't know if I'm the boxer or the bag
Location
Roanoke, VA.
Occupation
Sorta retired........
Right now some of the branch circuits have EGC with them and are terminated via a screw to the panel tub. Wasn’t sure if a separate ground buss should be installed.
I would use a ground bar. Most likely the screws used for the grounds are not machine thread screws and are not green.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Right now some of the branch circuits have EGC with them and are terminated via a screw to the panel tub. Wasn’t sure if a separate ground buss should be installed.
Take a look at 408.40
....Where the panelboard is used with nonmetallic raceway or cable or where separate equipment grounding conductors are provided, a terminal bar for the equipment grounding conductors shall be secured inside the cabinet....
 

dannyrzk

Member
Location
tulsa, OK
No need for a wire EGC then.
I would like to add another question here: what would happen if the existing conduit is underground and a continuity test shows the conduit is not operating as intended? In addition, there is no space inside the conduit to add an additional wire to be used as EGC. Thanks
 