I have a older building that has the conduit being used as the EGC. Now that I’m doing a major remodel do I have to put in ground bus and an EGC conductor with the the feeders?
Did you mean feeder or EGC? The feeder is in conduit (one listed in 250.118).Is the feeder a type listed on 250.118? If so, no
What do you mean by saying "put in a ground bus"?I have a older building that has the conduit being used as the EGC. Now that I’m doing a major remodel do I have to put in ground bus and an EGC conductor with the the feeders?
Right now some of the branch circuits have EGC with them and are terminated via a screw to the panel tub. Wasn’t sure if a separate ground buss should be installed.What do you mean by saying "put in a ground bus"?
Thanks for your help!No need for a wire EGC then.
I would use a ground bar. Most likely the screws used for the grounds are not machine thread screws and are not green.Right now some of the branch circuits have EGC with them and are terminated via a screw to the panel tub. Wasn’t sure if a separate ground buss should be installed.
Take a look at 408.40Right now some of the branch circuits have EGC with them and are terminated via a screw to the panel tub. Wasn’t sure if a separate ground buss should be installed.
....Where the panelboard is used with nonmetallic raceway or cable or where separate equipment grounding conductors are provided, a terminal bar for the equipment grounding conductors shall be secured inside the cabinet....
I would like to add another question here: what would happen if the existing conduit is underground and a continuity test shows the conduit is not operating as intended? In addition, there is no space inside the conduit to add an additional wire to be used as EGC. ThanksNo need for a wire EGC then.