There are grounding books that provide charts on the raceway size, and ocpd of contained conductors for the max length of metal raceways that may be used as a egc (not in the NEC). Also 250.122 (B)requires the egc to be increased in cma,. propotionally if the contained ungrounded conductors are increased for volatge drop.
As far as 250.4(A)(5) and (B)(4) are concerned a PE is better suited to explain this note. but it has to do with ampere squared seconds and a devices peak let thru. One table will give 1 amp for 5 seconds (I think) for every 42.25 cir mils of condcutor area (I think at 20 deg C) another Table uses 30cma (I think at 75 deg C) . Its a surviability (burn off) problem for the egc.
Again I don't have the book here but I'm sure someone does