busarvick
New member
- Williamsport PA
Is it legal per the code to make a Shepards hook type bend in any conduit?
I have been told by some other journeyman that goose necks or shepard hooks are illegal based on the bending radius being more than 90 degree's. They argue that the code says the max degree of bends is (4) 90 degree bends.
The max degree of bends is three hundred and sixty, you can put all three hundred and sixty of them in one big circle if you can bend pipe that good. I've never done a loopdy loop. I have used a shepards crook when the circumstances dictate a need.I have been told by some other journeyman that goose necks or shepard hooks are illegal based on the bending radius being more than 90 degree's. They argue that the code says the max degree of bends is (4) 90 degree bends.
Stick with what it actually says...I have been told by some other journeyman that goose necks or shepard hooks are illegal based on the bending radius being more than 90 degree's. They argue that the code says the max degree of bends is (4) 90 degree bends.
3xx.26 Bends ? Number in One Run. There shall not be
more than the equivalent of four quarter bends (360 degrees
total) between pull points, for example, conduit bodies and
boxes.