Does the flexible conduit connecting the motor at the end of a conduit run need to be included in the total degrees of bends in the run. Is there a code referance for this?
Does the flexible conduit connecting the motor at the end of a conduit run need to be included in the total degrees of bends in the run. Is there a code referance for this?
flex is not part of the conduit run imho
Flex is a conduit.
You can not have more than 360 degrees between pull points.
That is true.
However, one might interpret 300.18 to allow the flex to be not connected at the load end for utilization equipment "where required". The flex then may be considered to be straight, during the installation of conductors, if no obstructions exist.
As I read the 360 requirement I see it as applying at all times, once you connect the far end of the flex you still have to be under 360.
As I read the 360 requirement I see it as applying at all times, once you connect the far end of the flex you still have to be under 360.
is the load end of the flex not one of the "pull points", even while not connected to the equipment?
Sure, but once it is connected the requirement is still 360 before or after the conductors are in place.
IMO You cannot have more than 360 degrees between pull points even if you no longer have to 'pull'.
And I see it like Gus, install a C and move on.
It says "between pull points".
why is it called a "C"? Shouldn't it be a "S" for straight?
its called a 'C' because you see how easier it is to pull.![]()
Why not? One can argue that disconnecting the flex from the connector produces a pull point.am I forgiven?