Does the flexible conduit connecting the motor at the end of a conduit run need to be included in the total degrees of bends in the run. Is there a code referance for this?
 
Flex is a conduit.

You can not have more than 360 degrees between pull points.

That is true.

However, one might interpret 300.18 to allow the flex to be not connected at the load end for utilization equipment "where required". The flex then may be considered to be straight, during the installation of conductors, if no obstructions exist.
 
That is true.

However, one might interpret 300.18 to allow the flex to be not connected at the load end for utilization equipment "where required". The flex then may be considered to be straight, during the installation of conductors, if no obstructions exist.

As I read the 360 requirement I see it as applying at all times, once you connect the far end of the flex you still have to be under 360.
 
As I read the 360 requirement I see it as applying at all times, once you connect the far end of the flex you still have to be under 360.

I agree, one still has to be under 360 degrees. If we followed the other peoples logic, the when you do a run of rigid steel conduit and reach 360, you can connect emt to it without a box/elbow, in between and run another 360!! Thats insane.
 
As I read the 360 requirement I see it as applying at all times, once you connect the far end of the flex you still have to be under 360.

Maybe. But in section 348.26 the phrase is "between pull points". If the physical installation constraints require the installation of conductors before the final connection to the utilization equipment, is the load end of the flex not one of the "pull points", even while not connected to the equipment?

If not, where is the load-end pull point?
 
is the load end of the flex not one of the "pull points", even while not connected to the equipment?

Sure, but once it is connected the requirement is still 360 before or after the conductors are in place.

IMO You cannot have more than 360 degrees between pull points even if you no longer have to 'pull'.

And I see it like Gus, install a C and move on.
 
Sure, but once it is connected the requirement is still 360 before or after the conductors are in place.

IMO You cannot have more than 360 degrees between pull points even if you no longer have to 'pull'.

And I see it like Gus, install a C and move on.

Sure, me too, as long as it is smaller than AWG 4, anyway.

But it says what it says, and it doesn't say "360 before or after the conductors are in place". It says "between pull points". If the pull cannot be performed with the raceway connected, say to a motor termination enclosure ;), then the last bend likely does not exist when pulling.

And of course, I don't interpret it this way on my own jobs :cool:, I have my electricians count bends all the way to the ko, unless through an angle connector, as implied by 348.42.

What section are you using for this?
 
It says "between pull points".

Exactly what it says, and once you move the pull point by installing the flex you are violating what it says.

When you are done and look at the raceway between the pull points as they exist at that moment they must be under 360 degrees apart.
 
just for drill i never pull wire thru a flex. only up to the last fitting of the conduit and then slide the flex over the wire. never score the wire that way. am I forgiven?
 
I'm not Bob, but I say "done everyday and in violation of 300.18(A)"
 