We have an installation in an existing 2" Fiberglass conduit, using (12) 4Awg XHHW and (4) 8awg XHHW. The installation has an LB fitting. 314.16deals with 6Awg and smaller while 314.28 deals with 4Awg and larger. How do you calculate an LB fitting taht contains both?
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
I believe the LB's have a cu.in or a max wire size. A 2" LB says something like 4- 3/0 conductors-- I would calculate that and make sure my fill is no different
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Once you get to #4 and larger conductors you need to size the conduit body by using the 6X and 8X rules for pull boxes. The amount of fill is based on the conduit connected to it.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
Never seen one that said 4. Can't use them on 3Ø wye's. In fact I just had an install to a delta primary tranny. 3 500's in 3" EMT. Ordered 3" LB, only good for 3 300's. :blink: Used wireway.

I did say something like 4.... I was going from memory but mine sucks lately
 