jnthn00
Member
- Location
- lake elsinore, ca, usa
Does the MAX VOLUME inside an LL only apply if splicing conductors? I'm running a single 2.5" EMT from a distribution board to a panel, and the wire required is 4-4/0 and a #4G. My calcs bring the total cu in to 1.3772 and the max stamped is 3-250s (total cu in=157.3) Does this require me to upsize the LL to a 3.5"? I am not splicing.