N nathan1 Member Oct 19, 2004 #1 Is it code to support a 1"LB with 3/4 or 1/2 pipe as per 314.23(E)Exception. Thanks in advance.
don_resqcapt19 Moderator Staff member Location Illinois Occupation retired electrician Oct 20, 2004 #2 Re: Conduit body support 2 Conduit bodies with a trade size larger than the conduit and that have an internal volume of more than 100 cubic inches require independent support. Don
N nathan1 Member Oct 20, 2004 #3 Re: Conduit body support 2 Hey Don thanks....can i get an article number with that...how would you indepentently support an LB....thanks for your time.