Conduit body support

Status
Not open for further replies.

nathan1

Member
Does 314.23(E)exception mean that you cannot support an LB that is larger than your trade size conduit coming into the conduit body. If not I believe it states that this rule is for a conduit body with only one entry. What would this be??? Thanks in advance.
 
Re: Conduit body support

A conduit body with only one entry is an "E".
Check out a Crouse-Hinds or Appleton catalog to see one. You do not see many of them. They always make me think of the application where open wiring leaves a battery bank & then converts to a raceway system.
 
Re: Conduit body support

So in your opionon is it a code violation to conduet support a 1 inch LB by 3/4 or 1/2 inch emt.
 