Assuming conductors 4 AWG and larger, the conduit body only counts as a pull point, if it meets the requirements of 314.28. If the conductors are smaller, it will always count as a pull point.
 
Assuming conductors 4 AWG and larger, the conduit body only counts as a pull point, if it meets the requirements of 314.28. If the conductors are smaller, it will always count as a pull point.


Excellent point. I'm always seeing 4" EMT with a C conduit body in the middle of 8-90's. :slaphead:
 