Conduit bonding with class 3 circuits

Status
Not open for further replies.

Isaiah

Senior Member
Location
Baton Rouge
Occupation
Electrical Inspector
If a class 3 circuit is ran in a rigid galvanized steel conduit does the conduit still have to be bonded? The vendor supplied cable is being ran to (very low current) proximity switches in RGS conduit, which is also vendor supplied —But it’s not bonded.


Sent from my iPhone using Tapatalk
 
Based on 250.162 I would say no unless specifically required by a Code section relative to your installation.
 