Conduit Cable entries into the back of a NEMA 1 Panelboard Enclosure

Status
Not open for further replies.

JBR

Member
Location
LV NV
Occupation
Supervising CMI Electrical
What does code or UL say about Conduit or Cable (MC Cable) entry into the back of a Nema 1 Panelboard Enclosure
 
Are you asking if it's permitted? The answer is yes, you could use factory KO's or make your own.

Welcome to the forum. :)
 
Would you be able to provide a code reference? I always thought that it wasn't allowed either by NEC or UL?
 
I don't know of any general restriction on conduits running into the back of a panel enclosure (cabinet). There will be limitations based on the conductor size and 312.6.
 