steve-in-pa
Member
i am pretty confused with this subject. my plan- to add 4 receptacles in bedroom(2nd floor)all on one circuit.
my plan is is to come up from the basement with 12-2-2 romex, to a junction box on the attic floor. from there, i'd use 1/2inch emt(across attic wood floor) to 4 junction boxes, which would each be located over the bedroom wall below where i'd like to add a receptacle.
the 12-2-2 is going to be "half used.
the 12-2 part will feed the 4 new bedroom receptacles. if i have a tripping breaker(afci) i would use the "other half" of the 12-2-2.
in the 1/2 emt, i'd run thhn #12, with a green,black, and white. all 4 junction boxes/receptacles in paralell.
ques1- do i need to derate for any reason, or can 20amp afci be used?
ques2- if in future i use the 2nd half of the 12-2-2, and run another white and black in the 1/2inch emt, will i have to derate?
i'm running 12-2-2 in case i get stuck in future, and need a dedicated line, for air cond, computer, etc. if i do have to derate, would 3/4emt fix the derate problem?(be able to use 20amp afci? run length is prob 80'total.
I'd use 12-3 to get to the attic, and if a dedicated line was needed, i'd use a green,white,and2 hots, on a double pole breaker, but i'm afraid the afci's might get mixed up electronically, and trip when not supposed to/eratic bahavior. thanks for any help,info,advice.
my plan is is to come up from the basement with 12-2-2 romex, to a junction box on the attic floor. from there, i'd use 1/2inch emt(across attic wood floor) to 4 junction boxes, which would each be located over the bedroom wall below where i'd like to add a receptacle.
the 12-2-2 is going to be "half used.
the 12-2 part will feed the 4 new bedroom receptacles. if i have a tripping breaker(afci) i would use the "other half" of the 12-2-2.
in the 1/2 emt, i'd run thhn #12, with a green,black, and white. all 4 junction boxes/receptacles in paralell.
ques1- do i need to derate for any reason, or can 20amp afci be used?
ques2- if in future i use the 2nd half of the 12-2-2, and run another white and black in the 1/2inch emt, will i have to derate?
i'm running 12-2-2 in case i get stuck in future, and need a dedicated line, for air cond, computer, etc. if i do have to derate, would 3/4emt fix the derate problem?(be able to use 20amp afci? run length is prob 80'total.
I'd use 12-3 to get to the attic, and if a dedicated line was needed, i'd use a green,white,and2 hots, on a double pole breaker, but i'm afraid the afci's might get mixed up electronically, and trip when not supposed to/eratic bahavior. thanks for any help,info,advice.