Conduit connection

Charles99

Member
Location
Florida
Occupation
Electric
I have pvc conduit coming out of a concrete wall going into the back of a gutter box, but they’re too close together to get couplings on it. is there any code in the NEC that requires me to put a connector or can I cut a square in the back of the gutter and have them just going directly into it?


Sent from my iPhone using Tapatalk
 
I've seen what you've described many times with a pull box or a wireway. For either of those it is not code compliant. For an open bottom switchboard then yes you can do it that way.
 
Top