Recently I discovered that we have standard EMT using set screw couplings feeding 60 gas fired Infrared panels inside a cure oven for large parts. I know this is a mistake from a basic perspective but am trying to determine if this is considered class 1 div 1 or 2 location.
The Oven is fed by a 2 inch gas line branching off to feed the 60 small panels so the gas flow is significantly large. There is an exhaust fan system to evacuate fumes however not so much we cannot maintain temperatures of 330f.
My primary concern is with the conduits. The setscrew couplings come apart exposing the high temp wire to the edges of the conduit and coupling creating a wear hazard on the conductors. We plan to rewire the oven using rigid conduit. My secondary concern is if this does in fact meet Class 1 div1 or even 2 then we need seal offs and other techniques used to quarantine the explosion hazards of un burned gasses.
Please provide me with any feedback you may have regarding determining the classification rating of the ovens interior.
Thank you in advance
Sam
The Oven is fed by a 2 inch gas line branching off to feed the 60 small panels so the gas flow is significantly large. There is an exhaust fan system to evacuate fumes however not so much we cannot maintain temperatures of 330f.
My primary concern is with the conduits. The setscrew couplings come apart exposing the high temp wire to the edges of the conduit and coupling creating a wear hazard on the conductors. We plan to rewire the oven using rigid conduit. My secondary concern is if this does in fact meet Class 1 div1 or even 2 then we need seal offs and other techniques used to quarantine the explosion hazards of un burned gasses.
Please provide me with any feedback you may have regarding determining the classification rating of the ovens interior.