I am routing 4 - 3" conduits with 4 - 350kcmil conductors and 1 #4/0G in each conduit. The original plan was to provide 4 cores through a concrete wall but now they are placing a pull box on each side of the wall and only providing 1 core for all cables. They will just place a sleeve/nipple through the wall.
My understanding is that a 6" core is large enough for all these conductors and there is no de-rating for ampacity because the distance is less than 24".
Can someone please confirm my understanding is correct and this is acceptable?
Also, has anyone seen conduit larger than 6"?
Thank you.