I would like for someone to clarify the calculation involved in figuring out conduit fill using multi-conductor tray cable.
The way I understand it as it is stated in Chpt. 9, note 9 in the notes to the tables we use the 53% fill column from the appropriate catagory as it is treated as a single conductor. The area where I get confused is that it states in note 9 that we base the calc on the major diameter of the cable. Does that mean that we use the value given by the manufacturer of the wire and compare that to the appropriate 53% fill column or do we take the diameter (pi*rsquared) of that given value from the wire manufacturer and use that answer to compare?????
ex: A #6 Southwire 3c THHN/PVC, GW, TYPE TC POWER CABLE
It's ave. overall diameter in inches is .71(as per Southwires tables); The prints tell me to pull it into a 1" EMT conduit which is .458". To me this says a NO GO and I need to upsize to an 1 1/4". Or do I take the diameter calc of
.71" which is .3959" and I can use the 1" EMT.
Please Help :-?
The way I understand it as it is stated in Chpt. 9, note 9 in the notes to the tables we use the 53% fill column from the appropriate catagory as it is treated as a single conductor. The area where I get confused is that it states in note 9 that we base the calc on the major diameter of the cable. Does that mean that we use the value given by the manufacturer of the wire and compare that to the appropriate 53% fill column or do we take the diameter (pi*rsquared) of that given value from the wire manufacturer and use that answer to compare?????
ex: A #6 Southwire 3c THHN/PVC, GW, TYPE TC POWER CABLE
It's ave. overall diameter in inches is .71(as per Southwires tables); The prints tell me to pull it into a 1" EMT conduit which is .458". To me this says a NO GO and I need to upsize to an 1 1/4". Or do I take the diameter calc of
.71" which is .3959" and I can use the 1" EMT.