Conduit fill continuous non

Status
Not open for further replies.

Cletis

Senior Member
Location
OH
Is continuous / non a factor in conduit fill calcs ? If not why not?


Sent from my iPhone using Tapatalk
 
Is continuous / non a factor in conduit fill calcs ? If not why not?


Sent from my iPhone using Tapatalk

Not a factor. Derating is based on # of CCC tho, and they are assumed to carry the full load of the circuit(s), even when it's unlikely, like a 480Y system connected to 277V LED lights. If balanced (same number of lights on each phase, all 3 phases + neutral in the conduit), the neutral is not going to carry the same amps as the phase conductors, but must be counted due to the non-linear nature of the load.

Besides, continuous loads are already limited to 80% of the breaker's rating. Non-continuous loads could be sized up to 100% of the circuit ampacity.

Derating would be a nightmare if there were different tables and calcs for continuous and non-continuous loads if both circuits were in the same conduit.
 
Not a factor. Derating is based on # of CCC tho, and they are assumed to carry the full load of the circuit(s), even when it's unlikely, like a 480Y system connected to 277V LED lights. If balanced (same number of lights on each phase, all 3 phases + neutral in the conduit), the neutral is not going to carry the same amps as the phase conductors, but must be counted due to the non-linear nature of the load.

Besides, continuous loads are already limited to 80% of the breaker's rating. Non-continuous loads could be sized up to 100% of the circuit ampacity.

Derating would be a nightmare if there were different tables and calcs for continuous and non-continuous loads if both circuits were in the same conduit.