Here is the scenario......
1 1/2 EMT
61 # 12 THHN CCC's per Annex C Table C.1
Derating of CCC's per 310.15 (B) (2) (a) 30 X .35 = 10.5A
Can 20A OCPD's be used as long as the load is within the 10.5A allowed?
Also, I'm a little unclear about counting the grounded conductor as a CCC. In a situation where a common grounded conductor is serving three circuits originating from a three phase panel, would we count the grounded conductor as a CCC? What about a single phase situation with one grounded conductor serving two circuits? What about one circuit with one ungrounded and one grounded conductor? 310.15 (4) is a little hard for me to grasp. :x
1 1/2 EMT
61 # 12 THHN CCC's per Annex C Table C.1
Derating of CCC's per 310.15 (B) (2) (a) 30 X .35 = 10.5A
Can 20A OCPD's be used as long as the load is within the 10.5A allowed?
Also, I'm a little unclear about counting the grounded conductor as a CCC. In a situation where a common grounded conductor is serving three circuits originating from a three phase panel, would we count the grounded conductor as a CCC? What about a single phase situation with one grounded conductor serving two circuits? What about one circuit with one ungrounded and one grounded conductor? 310.15 (4) is a little hard for me to grasp. :x