hi guys i need a bit of clairifaction.
i have an engineer telling me i need to use the termination temp. rating of my breakers (75 degrees) to calculate my conduit fill. why??? arent these 2 totally seperate issues?
7-9#12 thhn in 310.15(b)(2)a calcs at 70%
#12 thhn the 90 degree column 30amps(for calc)= 21a
if i go to the 75 degree column it = 17.5a
i have an engineer telling me i need to use the termination temp. rating of my breakers (75 degrees) to calculate my conduit fill. why??? arent these 2 totally seperate issues?
7-9#12 thhn in 310.15(b)(2)a calcs at 70%
#12 thhn the 90 degree column 30amps(for calc)= 21a
if i go to the 75 degree column it = 17.5a